Tom,
We have lost input function on 3 different Konnect
boards, and here is how we have it set up:
- +24V on input
bank commons
- 7 normally
opened switches connected to input
- The other side
of the switch is connected to -24 ground
The input we are loosing is connected to switch
that is constantly on. It works fine for a few hours
and then stops working. The digital input screen
doesnt show any change when the switch is toggled. If
you look at the LED on the Konnect it comes on very
dimly. So dim you can hardly see it - a jumper
directly to ground has the same outcome.
When I change the input the switch is connected to
it starts working again, for a while, until that input
burns out to. This has happened on 3 boards with 2-4
inputs burning out on each Konnect. We hooked a
voltage analyzer to the 24V supply and tracked it
today - we lost two inputs. The voltage varies quite a
bit as we have 4 valves, a Keyence imaging camera,
lights, relays, and many sensors on the same circuit.
The high was 23.1 volts and the low was 21 volts.
The manual says the Konnect should handle 25 volts.
Do you have any idea why we could be loosing these
inputs? Maybe we are getting a voltage spike not being
picked up on our meter from one of the relay coils?
Perhaps we are running on the high end of the
optocoupler? We are getting a bit desperate to get our
equipment running again. Burning through boards pretty
quickly. Maybe add a resistor to the input bank
commons to drop our voltage down to the 5V range??
Any suggestions you have would be very helpful. We
are really struggling at the moment.
Thanks,
Scott